Enforcement Notice

Date of notice:
08/07/2022
Required compliance:
23/12/2022
Notice served to:
Andrea Khadari
Property type:
Other workplace
Applies to:
UNIT 28, 7 FOUNTAYNE ROAD, TOTTENHAM, LONDON, N15 4QL
Served to:
UNIT 28, 7 FOUNTAYNE ROAD, TOTTENHAM, LONDON, N15 4QL

Additional Information

Borough premises situated in: Haringey

Responsibility of person on whom notice served: Owner

Applicable legislation: Article 30: Regulatory Reform (Fire Safety) Order 2005

Articles

  • Article 8

    Failure to provide adequate fire separation between floors only.

    Provide adequate fire separation.

  • Article 9

    Failure to review the fire risk assessment.

    Implement regular program to review fire risk assessment.

  • Article 11

    Failure in the effective management of the preventive and protective measures.

    Implement arrangement for the effective planning, organisation, control, monitoring and review of the preventive and protective measures.

  • Article 13 Fire Fighting

    Failure to provide adequate means for fire fighting.

    Provide adequate fire fighting equipment.

  • Article 14

    Failure to ensure that emergency routes and exits are adequately lit.

    Ensure that adequate lighting is provided to illuminate emergency routes and exits.

  • Article 14

    Failure to provide and/or maintain adequate and clearly indicated emergency routes and exits that lead to a place of safety.

    Ensure that adequate escape routes and exits leading to a place of safety are provided and that these are maintained clear and available for use at all times that the premises is occupied.

  • Article 22

    Failure to co-operate with another responsible person(s) to co-ordinate measures required by the Order.