Enforcement Notice

Date of notice:
13/11/2024
Required compliance:
14/05/2025
Notice served to:
JK Group (UK) Limited
Property type:
Factory or warehouse
Applies to:
KANENDRA HOUSE, 22 ULLSWATER CRESCENT, COULSDON, CR5 2HR
Served to:
KANENDRA HOUSE, 22 ULLSWATER CRESCENT, COULSDON, CR5 2HR

Additional Information

Borough premises situated in: Croydon

Responsibility of person on whom notice served: Owner

Applicable legislation: Article 30: Regulatory Reform (Fire Safety) Order 2005

Articles

  • Article 8

    Failure to provide adequate fire separation between floors only.

    Provide adequate fire separation.

  • Article 9

    Failure to review the fire risk assessment.

    Implement regular program to review fire risk assessment.

  • Article 10

    Failure to apply the principles of prevention to the implementation of the preventative and protective measures identified by the risk assessment.

    Implement preventative and protective measures identified in fire risk assessment, on the basis of the principles of prevention.

  • Article 11

    Failure in the effective management of the preventive and protective measures.

    Implement arrangement for the effective planning, organisation, control, monitoring and review of the preventive and protective measures.

  • Article 13 Fire Warning

    Failure to provide a suitable method of giving warning in case of fire.

    Provide a suitable method of giving warning in case of fire.

  • Article 13 Fire Fighting

    Failure to provide adequate means for fire fighting.

    Provide adequate fire fighting equipment.

  • Article 13 Fire Fighting

    Failure to ensure non automatic fire fighting equipment is easily accessible/easy to use/indicated by signs.

    Provide easily accessible/easy to use non automatic fire fighting equipment that is indicated by signs.

  • Article 14

    Failure to provide and/or maintain adequate and clearly indicated emergency routes and exits that lead to a place of safety.

    Ensure that adequate escape routes and exits leading to a place of safety are provided and that these are maintained clear and available for use at all times that the premises is occupied.

  • Article 14

    Failure to ensure that emergency routes and exits are adequately lit.

    Ensure that adequate lighting is provided to illuminate emergency routes and exits.

  • Article 16

    Failure to ensure that information on emergency arrangements in respect of dangerous substances is available.

    Ensure that information on emergency arrangements in respect of dangerous substances is available.

  • Article 17

    Failure to ensure that the premises and any facilities, equipment and devices are maintained in an efficient state, in effective working order and in good repair.

    Ensure that adequate maintenance systems are in place to ensure that the premises and any facilities, equipment and devices are maintained in an efficient state, in effective working order and in good repair.

  • Article 18

    Failure to appoint sufficient competent persons to assist in undertaking preventive and protective measures.

    Appoint sufficient competent persons to assist in undertaking preventive and protective measures.