Enforcement Notice

Date of notice:
04/04/2023
Required compliance:
27/06/2023
Notice served to:
Mr John Watson-Miller
Property type:
Other workplace
Applies to:
330 ST JAMESS ROAD, LONDON, SE1 5JX
Served to:
, Ynni Ty Haf, Ty Haf Penybanc, Castlemorris, Pembrokeshire, SA62 5EL

Additional Information

Borough premises situated in: Southwark

Responsibility of person on whom notice served: Owner

Applicable legislation: Article 30: Regulatory Reform (Fire Safety) Order 2005

Articles

  • Article 8

    Failure to provide adequate fire separation between floors only.

    Provide adequate fire separation.

  • Article 9

    Failure to make a suitable and sufficient fire risk assessment.

    Carry out suitable and sufficient fire risk assessment.

  • Article 11

    Failure in the effective management of the preventive and protective measures.

    Implement arrangement for the effective planning, organisation, control, monitoring and review of the preventive and protective measures.

  • Article 13 Fire Warning

    Failure to provide a suitable method of giving warning in case of fire.

    Provide a suitable method of giving warning in case of fire.

  • Article 14

    Failure to provide and/or maintain adequate and clearly indicated emergency routes and exits that lead to a place of safety.

    Ensure that adequate escape routes and exits leading to a place of safety are provided and that these are maintained clear and available for use at all times that the premises is occupied.

  • Article 15

    Failure to establish an appropriate emergency plan.

    Prepare/update emergency plan.

  • Article 17

    Failure to ensure that the premises and any facilities, equipment and devices are maintained in an efficient state, in effective working order and in good repair.

    Ensure that adequate maintenance systems are in place to ensure that the premises and any facilities, equipment and devices are maintained in an efficient state, in effective working order and in good repair.